    Hello, i have Movicon 11 and Beckhoff CX 1020 Win CE6.0 problem is this i Movicon can read digital input on PLC, and can i visualise them, but can’t write on memory area on PLC. Where is problem?

    #132991
    MODERATOR
    Amministratore del forum

    Hello ,
    Any error in the logs file that can address in a better way on this issue?
    In the PLC have you set the “Q” memory area for this variable?
    Is the Movicon task configured as input/outpuy?
    BR
    Frank