  • #146217
    granzplast
    Partecipante

    When I import variables from the OPC UA server of the Schneider plc M251, the name of the variable starts automatically with “M241-M251 tag_name” as there is a space in the server name and the tag_name cannot operate with them, how can I solve it?

    #146228
    Brian_73
    Partecipante

    Hi Granzplast,
    Space char is not allowed in Movicon 11 variables name.
    But do you get an error when importing the tags? You cannot rename them without space on the OPC Server side.
    I know there is a “Var.Prefix” field you can use while importing, but I don’t think it’s useful in your case.

    Regards
    Brian

    #146242
    granzplast
    Partecipante

    When I import the variables I get them in this way:

    M241-M251 data_opc.tcp.variableName

    As you can see there is an space between M241-M251 and data, I tried to add an screenshot but it is not possible here.
    I would like to get the variables imported as: M241_M251_data_opc.tcp.variableName (as usually)

    Regards,