Movicon and CoDeSys 3 Connection

Movicon and CoDeSys 3 Connection

  • 6 marzo 2013 alle 1:08 pm #21008
    lgruz
    Membro

    Hi,
    We are testing Movicon since it might serve us for a project. We want to connect a PanelPC with Movicon to a PLC with CoDeSys, but we can’t. I’m trying with the OPC server included in CoDeSys 3 but when I try to connect, Movicon says ‘Failed!’. I tried to export symbols in ‘.sym’ format, but I do not find them in CoDeSys 3.

    What can I do?

    Thanks

  • 11 marzo 2013 alle 5:41 pm #21009
    Ian_C
    Membro

    Hi Igruz,

    The version 3 PLC need a 3S dll, in order to complete the connection. The GwClient.dll must be present in the client system, in the Supervisor directory or in a directory included in the path environment variable.
    In order to establish the connection with the PLC, a valid program must run and the program symbols must be exported

    Regards

  • 11 marzo 2013 alle 5:46 pm #21010
    lgruz
    Membro

    Thanks IAN_C,
    Finally I managed to connect both with the Codesys driver and with the OPC Client. It had a bit of mess with this topic.
    The principal problem was that I forgot to create the Configuration of symbols, and that I was not writing the Node address correctly.

    Thanks